I need to spec. a standby diesel generator, to
supply power to an office building, with computer equipment,
elevators, and HVAC units.
The office building is currently supplied by a
three-phase delta connected (secondary) single phase
transformer bank. The seconday voltage configuration
is 120/240V delta.
Each single phase transformer's secondary is 240 volt,
with 120 middle tap.
The phase A & C transformers are rated 50 KVA.
The middle phase B transformer is rated 100 KVA.
I am leaning towards sizing the diesel generator at 300 KVA,
with both an automatic start (on loss of power), and automatic transfer switch (to keep the generator from
backfeeding into the utility distribution system).
Any comments or suggestions?