I recently ran into a situtation where a service company entered the wrong COE for L. P. G. on an elec. meter so had to figure a product loss for the customer. I used the following formula Note; the Coe i used was for HD5 propane, with a spec. grav. of .505. you will ned to use a COE for fuel oil which is approx. .000025/Gal/oF. also you'll need the COE of the tank. This will help get you in the ball paBase temperature ie: (60oF) minus product temp. x c.o.e. factor ie

.00165) + 1 x Prover Volume
Ex. 1 60oF (base temp) minus 65oF (prover or product temp) x c.o.e. .00165 + 1 x prover volume (100.15) = 99.32
Ex. 2 60oF minus 20oF x .00165 + 1 x 100.15 = 106.76
Ex. 3 60oF minus 65oF x .0015 + 1 x 100.15 = 99.40
Ex. 4 60oF minus 20oF x .0015 + 1 x 100.15 = 106.16
Warning: Notice the difference @ 20oF between C.O. E. .0015 &
.00165 for just 100 gals. It is +.70 gallons (400%?!! more than PEI standards) , or meter would be in the customers favor by 7 gallons/1000, or 700 gallons for every 100,000 gallons. Be sure you know the correct C.O. E. for the product being tested. 20oF was used as an average do the fact the author believes in the upper midwest it is the average delivery temp. If your records show a colder/warmer average you can use the same formula.
For electronic meters with setup for linear S & linear F, carefully chooose the proper table and linear setting.
glm: Dan Gunn
Continued for deliveries closer to 0 oF:
Ex. 5 60 oF minus 1oF x .00165 + 1 x 100.15 = 109.90
Ex. 6 60 oF minus 1oF x .0015 + 1 x 100.15 = 109.01
Notice at 1o F a meter will not register approx. .90%, 0r 27 gallons for every 3,000 gallons deliveried when the C.O.E is set at .0015 instead of .00165 (the right coe for propane).
rk.