Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

Difference between Earthing Reactor and Earthing Transformer

Status
Not open for further replies.

haisa

Electrical
Oct 17, 2008
26
0
0
NG
Hello All.
We are installing a 150MVA 330/132/33kV Y/Y/D Transformer. Is using an Earthing Transformer and Earthing Reactor together appropriate on the Tertiary winding for protection?
 
Replies continue below

Recommended for you

By 'Earthing transformer' you mean a Zigzag winding transformer, I suppose. Normally, zigzag winding transformer is used to provide earth reference for an unearthed systems such as Delta tertiary side in the subject three winding transformer.
I have seen Resistor being connected to the neutral of the zigzag transformer but not reactor.
So, Zigzag earthing transformer and Earthing resistor are used together. Zigzag transformer to provide earth reference to the unearthed system and the neutral earthing resistor to limit the magnitude of the earth fault current in the system.

R Raghunath
 
The Earthing Reactor (Earthing Impedance) and the Earthing transformer are complimentary.
The earthing Transformer connects to the three phase grid to provide a single phase ground reference.
The Earthing impedance limits the ground fault current.

--------------------
Ohm's law
Not just a good idea;
It's the LAW!
 
If the tertiary is not loaded, one corner is kept earthed to avoid power frequency transferred overvoltages. An earthing transformer is used for extensive tertiary lines. Neutral earthing through the resistor is used to limit ground fault current, and the reactor is used to limit arc flash current in case of a ground fault in tertiary circuits. Normally, both are not required for the transformers mentioned by you.
 
Status
Not open for further replies.
Back
Top