Difference between RMU & MV switchgear

Status
Not open for further replies.

masalah

Electrical
May 10, 2010
27
0
0
QA
Dear all,

I need to know the differences between using RMU & MV switchgear. And when to use each one.
I think in RMU:

1) Not more than one TR can be used
2) Protection relays can't be as MV switchgear.
3) Looping manueavering is not available in RMU.

Are these correct? what are the correct differences? when each type shall be used?

My project is in Qatar, if this will make a difference in the answer.

Thank you.
 
Replies continue below

Recommended for you

With RMU solution (RM6 for example) you can have also more than one feeder, feeder in CB or disconnect+fuses you can also built a switchgear with some basic function. RMU is more compact and dedicated basic solution (for example for open loop in distribution) with basic or autonomous protection relay.
 