Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Difference between RMU & MV switchgear

Status
Not open for further replies.

masalah

Electrical
May 10, 2010
27
Dear all,

I need to know the differences between using RMU & MV switchgear. And when to use each one.
I think in RMU:

1) Not more than one TR can be used
2) Protection relays can't be as MV switchgear.
3) Looping manueavering is not available in RMU.

Are these correct? what are the correct differences? when each type shall be used?

My project is in Qatar, if this will make a difference in the answer.

Thank you.
 
Replies continue below

Recommended for you

With RMU solution (RM6 for example) you can have also more than one feeder, feeder in CB or disconnect+fuses you can also built a switchgear with some basic function. RMU is more compact and dedicated basic solution (for example for open loop in distribution) with basic or autonomous protection relay.
 
Check out the following thread: thread238-335075
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor