Dear All,
I have a problems on measuring the kWh consumption of a 3 phase motor with full load ampere of 5A since I measured difference kWh value with a Fluke 41B meter when I measure the reading at the main Distribution Board and near the motor.
The setup is as follows:
The main distribution board (for the whole floor of a building) is only supply electricity to a motor (since turn off all the other fuses in the main DB which provide to other equipments) which is running in unload condition Therefore, the power factor of it is just around 0.17. We take the reading at the main Distribution Board and near the motor with two Fluke 41B meter at the same time.
The result is as follows:
At Main DB:
Supply voltage: 386V
A rms: 2.85A
1.91kVA
0.32kW
1.87kVar
Power factor: 0.17
Sub DB near the motor:
Supply voltage: 386V
A rms: 2.75A
1.84kVA
0.34kW
1.80kVar
Power factor: 0.18
I would like to know why they have different power factor, KWh, kVAh and I rms between taking data on the main DB and the sub-DB?
I think that the utilities will count our consumption of electricity in the method of kVAh x site power factor. And if I put a sub meter for counting the power consumption , the kWh meter will calculate the kWh consumption in kVAh x p.f. of the motor? And some engineers told me that it is more accurate to count the consumption of the motor with using a kVAh meter? Moreover, I would like to buy a mechanical kVAh meter without other functions. Can you tell me where I can buy it?
Hope you can provide some opinions to me?
Thank you !
I have a problems on measuring the kWh consumption of a 3 phase motor with full load ampere of 5A since I measured difference kWh value with a Fluke 41B meter when I measure the reading at the main Distribution Board and near the motor.
The setup is as follows:
The main distribution board (for the whole floor of a building) is only supply electricity to a motor (since turn off all the other fuses in the main DB which provide to other equipments) which is running in unload condition Therefore, the power factor of it is just around 0.17. We take the reading at the main Distribution Board and near the motor with two Fluke 41B meter at the same time.
The result is as follows:
At Main DB:
Supply voltage: 386V
A rms: 2.85A
1.91kVA
0.32kW
1.87kVar
Power factor: 0.17
Sub DB near the motor:
Supply voltage: 386V
A rms: 2.75A
1.84kVA
0.34kW
1.80kVar
Power factor: 0.18
I would like to know why they have different power factor, KWh, kVAh and I rms between taking data on the main DB and the sub-DB?
I think that the utilities will count our consumption of electricity in the method of kVAh x site power factor. And if I put a sub meter for counting the power consumption , the kWh meter will calculate the kWh consumption in kVAh x p.f. of the motor? And some engineers told me that it is more accurate to count the consumption of the motor with using a kVAh meter? Moreover, I would like to buy a mechanical kVAh meter without other functions. Can you tell me where I can buy it?
Hope you can provide some opinions to me?
Thank you !