Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

% Difference of DC resistance in AC motor stators 1

Status
Not open for further replies.

electromike

Electrical
May 22, 2003
28
Does anyone know what an acceptable "Standard" percent difference of DC resistance one should find in LV 3 phase motor stators?
 
Replies continue below

Recommended for you

I should have stated the "Phase-to-Phase" DC resistance. Oops!
 
There should be no difference on a medium quality multi-meter.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
The instrument that you're using makes a difference on how you will apply a limit. In formal testing generally instruments with accuracy of 1 milliohm or better are specified. IEEE 62.2-2004 mentions an accuracy of 0.25% of reading.

Several motor repair and testing industry documents provide limits. Two terms I use related to comparing three meausurements for a 3-phase machine:
"Range" = (max – min)/average
"Deviation" = (Max Deviation from average)/Average
As a ROUGH rule to translate between these two terms, the range is twice the deviation.

Here are some winding resistance variation limits from various IEEE or EPRI specifications and documents. The 6 digit number list is the EPRI report number:


* Within 5% of each other (5% range, ~2.5% deviation) per EPRI 108773v1.
* Within 5% original value and 1% range (~0.5% deviation) per EPRI 107524
* EPRI Rewind spec 1000897 recommends a maximum 1% winding resistance deviation. Corresponds to approx 2% range.
* EPRI 111195 (MOV’s) – 5% from original factory data and 2% range (~1% deivation).
* EPRI 111196 (form wound) – 1/2% range (~1/4% deviation).
IEEE 1290 (MOV) PAGE E41 – 5% range (~2.5% deviation)
IEEE1415 states "The three values are compared—all readings should be within 3% to 5% from the average of the three readings". i.e. 3-5% deviation.

As you can see there is a spread of limits. The more accurate limits generally apply to larger motors and tested direct at motor. Less stringent limits apply to smaller motors and tested from the switchgear where cable can introduce variability.

=====================================
(2B)+(2B)' ?
 
Thanks for the info electripete! I am tring to "up" the skills of our technicians by introducing them to the concept of the phase-to-phase short ( I'm tired of the "Megger Test" being the final and only word on motor falures in my plant which thus causes un-needed drive change-outs ) and I found that I didnt have a good answer for what % difference they should look for.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor