Hello, dear friends

Could you help me whats is differente between ANSI/IEEE and IEC on altitudes Correction Factors ...?
what is a good option to aply on high altitude site, where the dielectric strength is less?
any opinion , information will help..!!

thx
mc



 
Replies continue below

Recommended for you

It's going to depend on the type of equipment you are interested in. There is not a single ANSI altitude correction factor.
 
The idea is how many of INSULATOR use in power line at high altitude side.
what is the best options up 2000 m ? which standart or other literature coul herlp me to choose the insulator with the better performance at this side?




 
If you're referring to strike distance correction or BIL de-rating for altitude...

I've always understood IEC to be +1% for every 100m over 1000m. IEEE basically follows the same up to 3000m (I think). Above 3000m it changes slightly.

 