cfox142
Structural
- Jun 22, 2015
- 18
I am looking at an existing building with composite metal deck and composite beams (shear studs). I am looking at the floor for some additional equipment to be added. From this I noticed that the composite deck capacities from Vulcraft and New Millennium vary quite a bit. The floor system is:
3" 20 Ga. Composite deck 5 1/2" total slab thickness spanning 10 ft over W16 beams with shear studs
In New Millennium this has a capacity of 203 PSF
In Vulcraft this has a capacity of 159 PSF
Does anyone know why the big difference? I assume the slab capacity is governed by the shear transfer at the slab to deck. Are the indentions in New Millennium deck larger or something? I look at the indentions in the deck as equivalent to shear studs on a beam i.e. larger sizes or quantities get a larger capacity until at some point you crush the concrete or yield the deck.
Thank you,
3" 20 Ga. Composite deck 5 1/2" total slab thickness spanning 10 ft over W16 beams with shear studs
In New Millennium this has a capacity of 203 PSF
In Vulcraft this has a capacity of 159 PSF
Does anyone know why the big difference? I assume the slab capacity is governed by the shear transfer at the slab to deck. Are the indentions in New Millennium deck larger or something? I look at the indentions in the deck as equivalent to shear studs on a beam i.e. larger sizes or quantities get a larger capacity until at some point you crush the concrete or yield the deck.