GGriffin
Mechanical
- Apr 11, 2018
- 7
Hi all,
I've been tasked to select a differential pressure switch for an exhaust application that only needs to determine whether there is airflow or not (no airflow signals an alarm). The low pressure input will be in the duct (perpendicular to airflow), the high pressure input will be ambient. Where I'm measuring is within the room the air is being exhausted from and has 250 cfm through an 8"x8" duct about 5' upstream from an exhaust grille.
What I'm having trouble with is what my actual operating differential is in order to select the proper model of switch. So far I have:
Using Bernoulli's equation,
_____Ambient______________Duct
P1 +1/2pV^2 + pgh = P2 + 1/2pV^2 + pgh
P1 - P2 = 1/2pV^2 = (0.5)*(1.204 kg/m^3)*(3.13 m/s)^2 = 1.88pa = 0.0076” w.c.
The lowest range on the switch is 0.03-0.10" w.c. which is above my calculated differential.
I'm wondering if the negative static pressure across the grille should be added to the calculated pressure differential? The fan upstream of my location is pulling air, the grille is resisting, so am I correct to assume that this will reduce the pressure further in the duct? Or does the fact that the fan is overcoming this static mean I should ignore it? The grille static pressure is 0.059" w.c. which would put me at 0.0666" w.c., and land within the lowest sensor range.
I can't find anything online explicitly helping with this issue so any advice is very much appreciated.
Thanks in advance,
GG
I've been tasked to select a differential pressure switch for an exhaust application that only needs to determine whether there is airflow or not (no airflow signals an alarm). The low pressure input will be in the duct (perpendicular to airflow), the high pressure input will be ambient. Where I'm measuring is within the room the air is being exhausted from and has 250 cfm through an 8"x8" duct about 5' upstream from an exhaust grille.
What I'm having trouble with is what my actual operating differential is in order to select the proper model of switch. So far I have:
Using Bernoulli's equation,
_____Ambient______________Duct
P1 +
P1 - P2 = 1/2pV^2 = (0.5)*(1.204 kg/m^3)*(3.13 m/s)^2 = 1.88pa = 0.0076” w.c.
The lowest range on the switch is 0.03-0.10" w.c. which is above my calculated differential.
I'm wondering if the negative static pressure across the grille should be added to the calculated pressure differential? The fan upstream of my location is pulling air, the grille is resisting, so am I correct to assume that this will reduce the pressure further in the duct? Or does the fact that the fan is overcoming this static mean I should ignore it? The grille static pressure is 0.059" w.c. which would put me at 0.0666" w.c., and land within the lowest sensor range.
I can't find anything online explicitly helping with this issue so any advice is very much appreciated.
Thanks in advance,
GG