Pitt03
Electrical
- Oct 15, 2015
- 18
Currently reviewing the protection and control in a new 13.8kV outdoor switchyard and was curious to hear if others would recommended implementing differential protection as part of the switchyard protection scheme.
This new switchyard is fed from an existing Utility substation (12MVA transformer) via a re-closer in the substation and several hundred yards of overhead Arial cable. The new switchyard has a main bus with two reclosers that feed two secondary buses (separated by tie switch). The secondary bus then has (4) reclosers which will then be used for underground feeders to a industrial process on the site. All equipment and distribution in the new switchyard is pole mounted and uses overhead cable.
My question is weather or not it makes sense to use differential protection anywhere between the existing substation and the 4 new outgoing feeders out of the switchyard. I've seen bus differential schemes used in substations before where bus was used but am not sure if it would make sense with overhead cable? Not sure if CT's used in re-closers could be used as part of a differential scheme either?
I was thinking it may make sense to have some sort of line differential on the long overhead line between the existing substation and the new switchyard?
There is also local 13.8kV generation nearby On-Site which will be used to feed the new Switchyard in emergency situations. Generator will connect at the new Switchyard through a tie switch at the switchyard and will likely have an output breaker located close to the generator. Would it make sense to use differential protection anywhere between the generator and the switchyard for faults that the generator backup protection may be slow to react to?