Recently, one of my oil filled transformer 13.8/4.16 kV, 5 MVA tripped by 87T (GE SR-745 Relay). This transformer worked in parallel with another identical 5 MVA transformer.
Relay's event record and phasors strongly indicated that there was single phase to ground fault in phase B LV side (attached below).
But insulation resistance test on the transformers and cables, WRM, TTR and DGA analysis shown no abnormality,
Is it possible that fault on transformer but the electrical and DGA test still shown good result? Thanks in advance