We have a transformer 15MVA, 132/11KV, Yy0. Primary CT ratio = 100/1A, Secondary CT ratio = 1200/0.577A.
We connected a differential scheme using Siemens ICTs (type 4AM22 20-7AA, T40/A) connected in star/delta on both sides. The primary was connected in 1:1 ratio using the windings 10:10 and the secondary in the ratio 1:1.732 using the windings 26:15.
The transformer trips at about 15% loading with this scheme. We connected so many similar schemes, either transforming LV current up or transforming HV current down. The result is always the same.
A scheme with which the transformer was able to carry a little above 50% of its rated capacity is connected as follows: HV ICT Ratio = 6/12, LV ICT Ratio = 7/8
With another scheme, the current into the relay from the HV side was almost equal in magnitude to the one from the LV side. But the two adds up instead of canceling.
Note: The transformer is solidly grounded on the HV side, and grounded through a resistor on the LV side. And there is REF connected to the neutral of the HV CTs. We are using three (Duo-bias) Electromechanical relays Reyrolle type C21).
We intend to create a floating Delta with the remaining ICT windings when we have a stable scheme.
The interposing CTs we are using are Siemens (type 4AM22 20-7AA, T40/A). The transformer was initially stable when the secondary CT was of ratio 800/1. After a fire incidence we installed a new secondary panel with a CT that has ratio of 1200/0.577 (Alstom type VMXspec BS/1S). After installing the new panel we were able to achieve a stable scheme after some manipulations, but right now not even that scheme is stable.
Can you please help me by suggesting what may be wrong with our design?
We connected a differential scheme using Siemens ICTs (type 4AM22 20-7AA, T40/A) connected in star/delta on both sides. The primary was connected in 1:1 ratio using the windings 10:10 and the secondary in the ratio 1:1.732 using the windings 26:15.
The transformer trips at about 15% loading with this scheme. We connected so many similar schemes, either transforming LV current up or transforming HV current down. The result is always the same.
A scheme with which the transformer was able to carry a little above 50% of its rated capacity is connected as follows: HV ICT Ratio = 6/12, LV ICT Ratio = 7/8
With another scheme, the current into the relay from the HV side was almost equal in magnitude to the one from the LV side. But the two adds up instead of canceling.
Note: The transformer is solidly grounded on the HV side, and grounded through a resistor on the LV side. And there is REF connected to the neutral of the HV CTs. We are using three (Duo-bias) Electromechanical relays Reyrolle type C21).
We intend to create a floating Delta with the remaining ICT windings when we have a stable scheme.
The interposing CTs we are using are Siemens (type 4AM22 20-7AA, T40/A). The transformer was initially stable when the secondary CT was of ratio 800/1. After a fire incidence we installed a new secondary panel with a CT that has ratio of 1200/0.577 (Alstom type VMXspec BS/1S). After installing the new panel we were able to achieve a stable scheme after some manipulations, but right now not even that scheme is stable.
Can you please help me by suggesting what may be wrong with our design?