According to ABB Switchgear Manual-11th revised edition/2006 VOL.13 chapter 13.2 Cables and wires PVC cable DIN-VDE 0271 it is now DIN-VDE 0276-603/627 and XLPE 0272 it is now 0276-603 also.
The rated current is shown in above standard. However the conversion factor for number of systems[f2] and ground thermal specific resistance, soil temperature and load factor[f1] is in VDE 0276-1000.
IEC 60502-1 does not recommend any current carrying capacity of low voltage cables but IEC 60364-5-52 does.
Let’s take an example of 3*240 mm^2 copper cable XLPE insulated PVC sheathed.
Conditions:90oC conductor temperature, load factor 1[100%] soil resistance 1 K.m/W soil temperature 20oC,number of cable, directly buried[ no conduits].
IEC 60364-5-52 does not make any difference between cable directly buried in soil or in conduit [So does BS 7671].VDE consider 85% for conduits.
The result:
DIN-VDE 428 A
IEC 414 A
It is interesting BS7671 following the same way as IEC the current carrying capacity it is only 382A.
NEC 2014 440 A-but for 0.9 K.m/W[90 oC.cm/W].