DIN/IEC - Cable Sizing

Status
Not open for further replies.

NickParker

Electrical
Sep 1, 2017
420
Hello,

The cable datasheet mentions it is manufactured according to DIN standard. It also mentions IEC standard in the same datasheet. Can I use IEC derating factors for these cables as my company only have IEC standards.
Din_Vs_iec_rhksbp.png
 
Replies continue below

Recommended for you

To be precise, you should get the cable de-rating table from the cable manufacturer/supplier. The IEC table is more broad based.
 
According to ABB Switchgear Manual-11th revised edition/2006 VOL.13 chapter 13.2 Cables and wires PVC cable DIN-VDE 0271 it is now DIN-VDE 0276-603/627 and XLPE 0272 it is now 0276-603 also.
The rated current is shown in above standard. However the conversion factor for number of systems[f2] and ground thermal specific resistance, soil temperature and load factor[f1] is in VDE 0276-1000.
IEC 60502-1 does not recommend any current carrying capacity of low voltage cables but IEC 60364-5-52 does.
Let’s take an example of 3*240 mm^2 copper cable XLPE insulated PVC sheathed.
Conditions:90oC conductor temperature, load factor 1[100%] soil resistance 1 K.m/W soil temperature 20oC,number of cable, directly buried[ no conduits].
IEC 60364-5-52 does not make any difference between cable directly buried in soil or in conduit [So does BS 7671].VDE consider 85% for conduits.
The result:
DIN-VDE 428 A
IEC 414 A
It is interesting BS7671 following the same way as IEC the current carrying capacity it is only 382A.
NEC 2014 440 A-but for 0.9 K.m/W[90 oC.cm/W].
 
Hi 7anoter,

Thanks!

7anoter4 said:
[/IEC 60364-5-52 does not make any difference between cable directly buried in soil or in conduit quote]

Tables B.52.18 and B.52.19 mentions the derating factor for cables buried directly in ground and cables laid in ducts/conduits respectively.
 
You are right. The table Table A.52-19 (52-E3) – Reduction factors for more than one circuit, cables laid in ducts in the ground- it presents reduction factors. However, the current-carrying capacities in amperes for methods of installation D [Table A.52-2 (52-C1) to A.52-5 (52-C4)] are for both[directly buried and laid in ducts].
See Table 52-3 (52H) – Examples of methods of installation providing instructions for obtaining current-carrying capacity item no. 70 up to 73.

 