NickParker
Electrical
- Sep 1, 2017
- 412
We have a LV switchgear where in the Incoming breaker, there is a trip unit which is of LSIG and also have a separate earth leakage relay.
Is it okay to disable the G function of the trip unit and use only earth leakage relay for earth/ground faults?
The reason is the G function cannot be set for low pickup, that is at 5A, while the spec calls to trip at 5A for ground faults in hazardous area.
Is it okay to disable the G function of the trip unit and use only earth leakage relay for earth/ground faults?
The reason is the G function cannot be set for low pickup, that is at 5A, while the spec calls to trip at 5A for ground faults in hazardous area.