Hello Everyone,
As some of you may know the latest draft of NFPA 70E 2021 has a new annex describing calculations for discharge times for capacitor banks.
The calculation process is pretty straightforward however the calculation method refers to a discharge resistance.
I have looked online at many manufacturer datasheets for capacitor banks and noticed they mention the expected discharge time but not the discharge resistance.
Out of curiosity, I am wondering if anyone out there may have some field experience with this topic.
When reading annex R from the latest NFPA 70E draft I get the impression the discharge resistance should be a known parameter.
I did find that Schneider electric has an FAQ on this item however based on their description I get the impression that the discharge resistance is built in per capacitor within the banks.
Their sample calculation shows an expected discharge resistance of 150 kohm connected in parallel to each capacitor.
Not sure if anyone can shed some light on how the discharge process actually occurs in the field.
Do most manufacturers typically provide a discharge time for capacitor banks?
Which then simply requires workers to de-energize the capacitor banks (after a risk assessment that is) and then wait for the indicated discharge time specified by the manufacturer?
Or
Are there cases where working personnel discharge the capacitors via some external discharge resistance?
If this is the case what's the process to determine the discharge resistance?
Link to the NFPA webpage with the latest draft of 70E 2021
Link for Schneider Electric Sample Discharge Resistance FAQ:
Image of Annex R Discharge Time Calculations
Sample Data Sheet from Eaton describing Discharge Time:
As some of you may know the latest draft of NFPA 70E 2021 has a new annex describing calculations for discharge times for capacitor banks.
The calculation process is pretty straightforward however the calculation method refers to a discharge resistance.
I have looked online at many manufacturer datasheets for capacitor banks and noticed they mention the expected discharge time but not the discharge resistance.
Out of curiosity, I am wondering if anyone out there may have some field experience with this topic.
When reading annex R from the latest NFPA 70E draft I get the impression the discharge resistance should be a known parameter.
I did find that Schneider electric has an FAQ on this item however based on their description I get the impression that the discharge resistance is built in per capacitor within the banks.
Their sample calculation shows an expected discharge resistance of 150 kohm connected in parallel to each capacitor.
Not sure if anyone can shed some light on how the discharge process actually occurs in the field.
Do most manufacturers typically provide a discharge time for capacitor banks?
Which then simply requires workers to de-energize the capacitor banks (after a risk assessment that is) and then wait for the indicated discharge time specified by the manufacturer?
Or
Are there cases where working personnel discharge the capacitors via some external discharge resistance?
If this is the case what's the process to determine the discharge resistance?
Link to the NFPA webpage with the latest draft of 70E 2021
Link for Schneider Electric Sample Discharge Resistance FAQ:
Image of Annex R Discharge Time Calculations
Sample Data Sheet from Eaton describing Discharge Time: