All the manufacturer (to my knowledge so far) give the static accuracy of the distance protection relay at the reach point, at line angle.
In practice the tolerance is not defined for all the characteristcs (unless you take the accuracy data for voltage and current measurement, and get crazy to translate it in an impedance error...).
More: test sets define the accuracy lines in their own way. 5% here is not the same as 5% there..
Are you also in this black hole? Any idea on how to get out of it? Or.. do we need to get out of it?