To change the direction that the relay sees as forward, you need to swap the polarity of either the CT's or the VT's.
Please bear in mind that there is more than one way to misconnect the instrument transformers to the relay. You have a numerical protection relay, which makes confirming CT connections a breeze. If the system is already in service, then go and check the phasors online and compare with what you would expect (perhaps compare to metering or another relay on the same line?). For new relays, we often use line charging current after first energisation to gather phasor information.
From this, you should be able to work out exactly how your relay is misconnected (if at all), rather than a "try it and see" approach.