Distillery Ethanol process and Storage Tanks

Status
Not open for further replies.

Bill3752

Chemical
Jan 24, 2008
138
I have come across some distilleries that are applying NFPA as follows to atmospheric tanks (designed to 1 oz/in2:
1. Have automatic sprinkler systems - F factor = .3.
2. There is verbiage in NFPA that states that for ethanol can take another 50% reduction on top of that - i.e. F factor = .15.

Anyone have experience with this? Must tanks be designed to a specific standard to incorporate this?

Off hand, taking this level of credit scares me.

 
Replies continue below

Recommended for you

Doesn't NFPA require the fire protection to be a Fixed Waterspray System meeting NFPA 15?

A sprinkler system meeting NFPA 13 with normally closed sprinkler heads isn't equivalent to a waterspray system with open nozzles.
 