Dear All,
we have 3 padmount distribution transformers , rated for 13.200Y / 208y-120.
the line voltage in Haiti is 12.470v.
we keep on experiencing low secondary voltage , and the installer of the transformer tell us that it is because of grid power , not transformer.
my guess is that the transformation ratio is 13.200/208 = 63.5
the secondary voltage should be 12470 / 63.5 = 196v.
am I right ?
maybe we can adjust the tap on the transformers , 196v + 5% = 206v
what do you think ?
thanks for the support.
best regards
Jean Michel