Hello,
I have a question about DLO insulation Rating.
I always used them before into 600V distribution. So i never cared about the insulation rating of 1000V vs 2000V.
But, into an installation, the 2kV insulation rating is required, but this is not a typical rated voltage for cables in Canada. It is more an American voltage standard from my experience browsing UL cable catalogues.
So when i look into a datasheet like this one:
Do you think CSA authorizes the use of DLO at 2kV in Canada instead of limited to 1kV?
My personel research led me to a yes.
CSA C22.2 No. 38 mentions a minimum insulation level of 1.14 mm for 2000V cable, and this one in the datasheet has 2mm, so i believe i have my answer.
Just curious to know what anybody else thinks about this?
Thank you!
Julien