Should we activate zero sequence current elimination in differential relays for a YnD11 power transformer with a zig-zag grounding transformer on the delta side and grounded on the star side ?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
RRaghunath said:It is YNd11 Step-down transformer, with a Zigzag transformer on delta side providing earth reference.
Everyone agrees Zero sequence filtering is to be selected on Y-side.
With regard to Delta side, it depends on how the Zigzag transformer is connected.
# If Zigzag transformer is connected at transformer terminals and the CTs are located in the switchgear incomer panel, zero sequence filtering is required.