We have a 2500kVA/2800kVA 55/65 deg C oil filled tranformer that sits outside of the switchgear room where it feeds a 480V switchgear that feeds two large power users that consume about 2000kVA.
This is in the Midwest part of the USA, where routinely the temperatures in the summer approach 100deg. Per the NEC cables have to be derated based on that temp is it the same with transformers?
They are talking about increasing the load so that it will consume 2400 kVA, over 90% of the capacity on the 55deg temp capacity. I'm questioning if this is a good move on an old transformer as this is.
I thought you weren't to load a transformer but to 80% and not to use mechanical means of cooling except for peaks, these loads however are continuous.
Any equation I can use here to prove that we shouldn't do this without bumping the size of the transformer?
This is in the Midwest part of the USA, where routinely the temperatures in the summer approach 100deg. Per the NEC cables have to be derated based on that temp is it the same with transformers?
They are talking about increasing the load so that it will consume 2400 kVA, over 90% of the capacity on the 55deg temp capacity. I'm questioning if this is a good move on an old transformer as this is.
I thought you weren't to load a transformer but to 80% and not to use mechanical means of cooling except for peaks, these loads however are continuous.
Any equation I can use here to prove that we shouldn't do this without bumping the size of the transformer?