Basler provided printouts of their relay settings for new relays that replaced old ones in some old switchgear.
They specified E2 - IAC Extremely Inverse. EasyPower does not have that pick. It has: E2 - Extremely Inverse and C1 - IEC Extremely Inverse.
Note they specified IAC ... which isn't IEC.
Side by side, for the exact same settings the curves are way different.
They specified E2 - IAC Extremely Inverse. EasyPower does not have that pick. It has: E2 - Extremely Inverse and C1 - IEC Extremely Inverse.
Note they specified IAC ... which isn't IEC.
Side by side, for the exact same settings the curves are way different.