Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Does NFPA 13 address unpackaged bulk storage such as piled grain warehouse? 1

Status
Not open for further replies.

Alireza01

Mechanical
Feb 14, 2017
14
Hi
I didn't find any regulation about automatic fire protection system design for unpackaged bulk storage such as piled grain warehouse.
Is it effective to install sprinkler system for such these warehouses?
Is there any criteria for such system design (like NFPA 13)?


 
Replies continue below

Recommended for you

There are some few references to granular materials in table A.20.4(b) of NFPA 13
 
Alireza01:

FM Global has a loss and prevention sheet on this subject - 7-75.

Link

Regards,

DB
 
Thank you for your replies.
I have some uncertainties about sprinkler system consideration for high roof piled grain warehouses.
1- Since the combustible contents of the warehouse are not integrated solid substances (particulate solid) and possible fire is a surface fire, So I think spraying water is not very effective ( Water is quickly transferred to the bottom of the grain mass)
2- Due to the height of the roof (about 12m), will the heat of the fire cause the sprinkler to activate?
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor