HVmazz
Aerospace
- Jun 26, 2007
- 8
I have a proposal to install a replacement (~pump cost = $4,000) 10 Hp water pumping system which is serviced with an Open Delta three phase 240 volt 50 KW utility supply. The old system has experienced three motor burn-outs in the last 4 years. The new motor is rated at 10 Hp, 230 volt, three phase, 28 F.L.A.and has a manufacturers 5 year/10,000 Hr. warranty. I will be adding phase loss/reversal, over, under & unbalanced voltage & short cycling monitoring to the control panel. The manufacturer will honor the full warranty ONLY if "...the 230 volt/3 phase 60 Hz power source is a good dependable supply and NOT originating from an Open Delta power circuit". The utility company engineering department claims this type of service is normal and wants $5,000 to add the third transformer to the service to yield 208/120 three phase which would also require a new motor selection. We also have a small single phase lighting load. The pump manufacturer will make changes to the motor windings to accomodate the 240 Volt Open Delta supply. How much will the pump life be shortened running on an Open Delta source? Should we add our own transformer on the secondary side?