  • Congratulations Toost on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!
Does Partial Discharge Test Make Hi-Pot Unneccesary? 7
FEinTX
25
We are building a wind farm with a 34.5 KV collection system. The contract calls for hi-pot testing prior to energization of all circuits. In addition to the hi-pot, the customer has recently decided to have the entire collection system tested by a reputable firm using Partial Discharge equipment/analysis.
Question (1): Is there any added value to doing the hi-pot test, or would this now be unnecessary?
I've been told that a PD test will catch everything that a hi-pot will, and more, but need to be sure before deciding to skip the hi-pot.
Question (2): Are there any potential risks to doing a 1.5X hi-pot test on brand-new cable?
I am aware that hi-potting can lead to premature failure on cable with early-stage water penetration, but I'm not sure if there are risks if the cable is newly laid.
Thanks for any clarification you can offer!
FEinTX
Zogzog,
I believe I understand your question much better now. Your question is a good one. No test can predict if a cable is going to be mistreated and over heated. However, some conduction types of defects can produce localized heating. This is a very low probability event in extruded insulation (plastic and rubber) but, there is a substantial probability in paper insulation. With the data I have seen, I would say that the chance of detecting conduction defects with a DC test in extruded cable systems (such as the systems at wind farms) is less than 1%.
Benjamin Lanz
Vice Chair of IEEE 400
Sr. Application Engineer
IMCORP- Power Cable Reliability Consultants