Domestic Allowance
TravisMack
This is truly a question for a friend :-)
When doing a large apartment complex per NFPA 13R (say 16 buildings where each are appropriate for 13R) that is supplied by a common fire loop, what do you do for the domestic allowance? This particular site had a domestic booster pump placed on the site for the domestic/fire loop. The sprinkler demand is 80 gpm +/- for the 4 residential sprinklers.
Since this is a domestic/fire loop 13R states that you have to figure a domestic allowance. My conservative nature says that you should figure the domestic load for each building on site and include that in the loop with your fire sprinkler flow. The reasoning is that if this is a fire in building #1, people will likely still be doing dishes, using bathrooms, showers, etc in most of the other buildings. So, that pump is still going to be supplying that demand.
However, NFPA 13R states that you just figure the individual building where you have a combined fireline for the building. My thought is that would be like a single small condo or something where you have the domestic and fire split in the building. This particular project has separate fire lines and domestic water lines to each building.
The main problem on this project is that the sprinkler guy only figured the sprinkler demand for the individual building and used the pump at the left hand side of the curve. There was like 50 psi or so at the street, then boosted with 80 psi @ 500 gpm pump. Well, since the sprinkler demand was so low, he basically had 130 psi to deal with. Now, the AHJ has come back and stated that he wants the domestic load included. The domestic load based on the table in NFPA 13R (A9.6) will be about 400 gpm for this complex. So, they end up losing about 20 psi of total supply pressure. As you can imagine, the system is installed (prior to permits - VERY BAD IDEA) and now none of it works. Due to the very high pressures they thought were available, the lead-ins were installed as 1" pipe, and all 1" and 3/4" cpvc.
So, basically, how would you guys interpret the domestic load that is needed?
Travis Mack
MFP Design, LLC
"Follow" us at
Yeah. I received the NFSA informal interp as well. Unfortunately, the AHJ doesn't agree with this interp and is requiring the MEP engineer provide a calculation for total domestic demand. That is then to be added to the fire sprinkler demand and have it flow through the loop/pump system.
I also believe that is the most correct way to handle the situation.
Travis Mack
MFP Design, LLC
"Follow" us at
Yeah,
I too feel the interpt does not match the wording in the code. It (6.5.5) doesn't distinguish between private and public. You can get the definition of private fire service main from 14.
However, there is no mention in the section where this is discussed. As I previously alluded, the annex further explains that all devices downstream Of Any Point of the supply are to be counted.
Even the preferred arrangement detail could be supply to 100 other buildings. It may be Assumed to be to one building.
However, as Travis stated, this is the best way. Let's ask the question, If there is a fire, could the other buildings be using water that could rob the system?
R/
Matt
That is the exact point, Matt.
If this were just a single building, performing the flow test at the estimated peak usage time would account for all of the domestic load on the city main. After all, our static readings on a flow test are not true "static" conditions. It is already accounting for any use of the line at that point in time.
This has been an interesting thread and discussion on how to view these, to be sure.
Since this is all installed, I keep telling them to either get a flow test at the peak usage time, or just have the MEP engineer calculate the domestic load and add it to the sprinkler system. This seems to be one of those situations where no one wants to act and is hoping some one else will do the work to solve the problem. I hate those situations!! ACT MAN!! ACT!!!
Travis Mack
MFP Design, LLC
"Follow" us at
Oh how I miss the 24 hour meter days. Take the lowest pressure for a 30 minute duration...
R/
Matt
Yeah. That was one of the first suggestions. Get a 24 hour recorder. Leave it on for a week. You can figure when is the greatest usage time. Then do your flow test. Some things are just too easy.
Travis Mack
MFP Design, LLC
"Follow" us at
Greatest usage time is halftime during the Superbowl :-)