After reading the IEEE STD 1036-2010 refaurding the use of shunt capacitor banks on power systems there still remains an issue I am unsure of. The standard provides a formula to calculate the peak inrush current in a double bank energizing scenario, I have the following question's wich need some clarification if anyone could assist. The formula only considers the impedance between the two banks.
1 Why does IEEE choose not to add the nominal bank current at 60Hz to the higher frequency inrush current at say 3000Hz surely when the 50hz peaks and the 3000Hz peak at the same time this is the worst case
2.What about the transient current that will momentarily flow between the two banks in parallel and the source impedance of say 1000Hz (should this not be included aswell)
basically would the worst case condition not occur when all three of theses currents peak at the same time ?
thanks
After reading the IEEE STD 1036-2010 refaurding the use of shunt capacitor banks on power systems there still remains an issue I am unsure of. The standard provides a formula to calculate the peak inrush current in a double bank energizing scenario, I have the following question's wich need some clarification if anyone could assist. The formula only considers the impedance between the two banks.
1 Why does IEEE choose not to add the nominal bank current at 60Hz to the higher frequency inrush current at say 3000Hz surely when the 50hz peaks and the 3000Hz peak at the same time this is the worst case
2.What about the transient current that will momentarily flow between the two banks in parallel and the source impedance of say 1000Hz (should this not be included aswell)
basically would the worst case condition not occur when all three of theses currents peak at the same time ?