gregdachs
Mechanical
- Jun 14, 2004
- 10
We have a boiler with a 10' Clarage draft fan. Right now, the fan is throttled primarily by use of the inlet dampers. We have noticed that the fan has vibration that increases at night. The shaft is balanced and well mounted and the rest of the system seems ok, so we have concluded that the problem is possibly caused by an aerodynamic instability caused by the denser air.
The proposed solution to this is to switch to throttling with the outlet dampers. I am about to argue against this, but given that I hadn’t seen a fan curve until Friday I thought I would make sure I was on the right track. Wouldn’t throttling with the outlet dampers serve to increase the density of the air contained within the fan body because it is pressurizing it slightly against the outlet dampers?
Any suggestions would be greatly appreciated. Also, if anyone can think of a more logical reason for our problem I’d love to hear it.
-Greg
The proposed solution to this is to switch to throttling with the outlet dampers. I am about to argue against this, but given that I hadn’t seen a fan curve until Friday I thought I would make sure I was on the right track. Wouldn’t throttling with the outlet dampers serve to increase the density of the air contained within the fan body because it is pressurizing it slightly against the outlet dampers?
Any suggestions would be greatly appreciated. Also, if anyone can think of a more logical reason for our problem I’d love to hear it.
-Greg