Hi,
I have a drilled pier which needs to extend all the way to rock per geotech report for the bearing. The diameter for the drilled pier that I am coming up with is a 4'-0" based on loads. The rock profile is 70'-0" down, which means the drilled pier length will be +/- 70'. IBC 2012, 1810.2.2 calls out minimum 3 piles attached with rigid cap for stability requirements. There is an exception to this stating if the drilled pier is greater than 2'-0" in dia and the adequate lateral support is provided for the entire height and the height does not exceed 12 times least horizontal dims.. I am getting stuck with "height does not exceed 12 times least horizontal dims". Does this mean the min dia I need to use is 6'-0" even though the 4'-0" dia is more than sufficient for load carrying capacity satisfying all limit states.
I have a drilled pier which needs to extend all the way to rock per geotech report for the bearing. The diameter for the drilled pier that I am coming up with is a 4'-0" based on loads. The rock profile is 70'-0" down, which means the drilled pier length will be +/- 70'. IBC 2012, 1810.2.2 calls out minimum 3 piles attached with rigid cap for stability requirements. There is an exception to this stating if the drilled pier is greater than 2'-0" in dia and the adequate lateral support is provided for the entire height and the height does not exceed 12 times least horizontal dims.. I am getting stuck with "height does not exceed 12 times least horizontal dims". Does this mean the min dia I need to use is 6'-0" even though the 4'-0" dia is more than sufficient for load carrying capacity satisfying all limit states.