I have an old 3 story hotel that has a walkway that loops the entire building for 3 floors and is exposed to the elements. Think of an old hotel where the stairs are exposed and so is the wrap around covered walkway.
Our thought we be to install a new dry system that is installed and loops this walkway and then run lines into each room. They are converting it to homeless shelter. My issue is with the system size, the Dry system will easily be over 750 gallons per floor so I am thinking about diving each floor into 2 systems.
But then I run in NFPA 13 (2013) section 7.2.3.1.1 which states that any dry pipe system protecting dwelling unit portions of any occupancy shall deliver water in 15 seconds to the test connection. It also states that I cannot use sections 7.2.3.2, 7.2.3.3, 7.2.3.4, but I can use 7.2.3.5 which talks about dry pipe systems being calculated for delivery times per Table 7.2.3.6.1
So am I going to be stuck with 15 seconds or can I use the table under light hazard for 60 seconds delivery time?
Thanks for the help!
Our thought we be to install a new dry system that is installed and loops this walkway and then run lines into each room. They are converting it to homeless shelter. My issue is with the system size, the Dry system will easily be over 750 gallons per floor so I am thinking about diving each floor into 2 systems.
But then I run in NFPA 13 (2013) section 7.2.3.1.1 which states that any dry pipe system protecting dwelling unit portions of any occupancy shall deliver water in 15 seconds to the test connection. It also states that I cannot use sections 7.2.3.2, 7.2.3.3, 7.2.3.4, but I can use 7.2.3.5 which talks about dry pipe systems being calculated for delivery times per Table 7.2.3.6.1
So am I going to be stuck with 15 seconds or can I use the table under light hazard for 60 seconds delivery time?
Thanks for the help!