SherifH
Mechanical
- Mar 19, 2020
- 2
thread184-444593
I was reading this thread and its quite confusing and has conflicting points. I wanted to revive it and give a more detailed explanation as to the question so that its understood correctly, to hopefully attract more relevant discussion and be able to obtain a more assuring conclusion.
The Facts
1) A Dry Standpipe system exists.
2) The water supply pressure (city water pressure) is too low to be self-sufficient and thus needs a NFPA-20 Fire Pump.
3) An air compressor ensures adequate air pressure downstream of the air valve to keep it closed.
4) The Fire Pump & Alarms are triggered only when the Air Valve is opened, i.e the air pressure downstream falls enough that the water pressure upstream pushes the seat. (I do not know if this one is correct, its my understanding)
Is a jockey pump still required UPSTREAM of the air valve with the fire pump, or can the fire pump function alone?
I want to know your opinions on the following logic:
A) If there is a drop in city water pressure, the air valve will not be opened. If the fire pump is only triggered on an opening of the air valve, this tells me that a jockey pump is not required. (This goes back to assumption stated in #4 above, because if the fire pump is also activated by a loss of water pressure this would not apply). As such, a jockey pump is not required.
On the other hand, if the water pressure upstream of the air valve drops, then consequently that would mean that the air pressure drop would have to be bigger downstream to open the valve which could cause problems since this would mean a delayed response to a fire.
B) A drop in city water pressure as an issue can be indicated by a pressure gauge that would alert operators there is something wrong (leaking) without having to trigger the alarm system. The jockey pump here would keep pressure through the leak, but if they are alerted and manage to fix the issue, the pipe shall go back to city water pressure and thus a jockey pump can still be avoided.
Unless it is mandated by the NFPA or Building Code for reasons im unaware of atm.
Looking for some insight or some previous experience Please & Thanks!
I was reading this thread and its quite confusing and has conflicting points. I wanted to revive it and give a more detailed explanation as to the question so that its understood correctly, to hopefully attract more relevant discussion and be able to obtain a more assuring conclusion.
The Facts
1) A Dry Standpipe system exists.
2) The water supply pressure (city water pressure) is too low to be self-sufficient and thus needs a NFPA-20 Fire Pump.
3) An air compressor ensures adequate air pressure downstream of the air valve to keep it closed.
4) The Fire Pump & Alarms are triggered only when the Air Valve is opened, i.e the air pressure downstream falls enough that the water pressure upstream pushes the seat. (I do not know if this one is correct, its my understanding)
Is a jockey pump still required UPSTREAM of the air valve with the fire pump, or can the fire pump function alone?
I want to know your opinions on the following logic:
A) If there is a drop in city water pressure, the air valve will not be opened. If the fire pump is only triggered on an opening of the air valve, this tells me that a jockey pump is not required. (This goes back to assumption stated in #4 above, because if the fire pump is also activated by a loss of water pressure this would not apply). As such, a jockey pump is not required.
On the other hand, if the water pressure upstream of the air valve drops, then consequently that would mean that the air pressure drop would have to be bigger downstream to open the valve which could cause problems since this would mean a delayed response to a fire.
B) A drop in city water pressure as an issue can be indicated by a pressure gauge that would alert operators there is something wrong (leaking) without having to trigger the alarm system. The jockey pump here would keep pressure through the leak, but if they are alerted and manage to fix the issue, the pipe shall go back to city water pressure and thus a jockey pump can still be avoided.
Unless it is mandated by the NFPA or Building Code for reasons im unaware of atm.
Looking for some insight or some previous experience Please & Thanks!