I have a problem with relay protection settings for two dry type transformers 6/0,4 kV, 2000 kVA.
Problem is in very high (according to me) inrush currents and very long period of the process. Transformers are protected by 7SJ62 relays (Siemens). No problems with O/C protection as 2-nd harmonic blocking is used. But we have several trips during the commissioning from E/F protection. Transformers were switched on off-load several times and sometimes they trip, sometimes not. You can see disturbance records in COMTRADE format. Earth fault current is measured via CT's connected in star (no cable-type transformer). E/F protection trips from unbalanced currents during the energizing process.
What makes me to worry is the high level of magnetizing currents and long periods of the process. On the records they are cut after approx. 300 ms, but due to E/F trip. Colleagues from site reported for processes longer than 1 s and phase currents over 1100 A, with unbalanced current in E/F input more than 150 A (E/F protection temporary disabled). It seems quite high values for me. From my experience the heaviest inrush I have found was on 40-years old Chinese oil-filled transformer, and it was not so heavy as these ones. I have no experience with dry transformers. I have listened that their magnetizing is harder than oil-filled trafos.
Any advice how to solve the problem will be very helpful.
------------------------
It may be like this in theory and practice, but in real life it is completely different.
The favourite sentence of my army sergeant
Problem is in very high (according to me) inrush currents and very long period of the process. Transformers are protected by 7SJ62 relays (Siemens). No problems with O/C protection as 2-nd harmonic blocking is used. But we have several trips during the commissioning from E/F protection. Transformers were switched on off-load several times and sometimes they trip, sometimes not. You can see disturbance records in COMTRADE format. Earth fault current is measured via CT's connected in star (no cable-type transformer). E/F protection trips from unbalanced currents during the energizing process.
What makes me to worry is the high level of magnetizing currents and long periods of the process. On the records they are cut after approx. 300 ms, but due to E/F trip. Colleagues from site reported for processes longer than 1 s and phase currents over 1100 A, with unbalanced current in E/F input more than 150 A (E/F protection temporary disabled). It seems quite high values for me. From my experience the heaviest inrush I have found was on 40-years old Chinese oil-filled transformer, and it was not so heavy as these ones. I have no experience with dry transformers. I have listened that their magnetizing is harder than oil-filled trafos.
Any advice how to solve the problem will be very helpful.
------------------------
It may be like this in theory and practice, but in real life it is completely different.
The favourite sentence of my army sergeant