Wellhead panels operate in many cases on fuel gas. In several cases the separation of condensate or oil from the fuel gas supply has proved inadequate resulting in damaging the equipment or malfunction.
It is desired to improve the fuel gas by knocking down the heavy hydrocarbons and moisture (if present) at remote location.
The typical composition of gas at wellhead is here under:
Component Mole %
>H2S 0.0
>CO2 1.43
>N2 14.9
>C1 51.24
>C2 7.72
>C3 8.25
>C4 4.01
>C4 5.69
>C5 3.12
>C5 2.07
>C6 1.27
>C7 + 0.3
>Total 100%
Operatining pressure minimum 85 Max. 100 psig
>Design pressure 150# rating
>Design Temp 150 deg. F
>Operating TEmp 115 deg. F
>Liquid Spec. Gr 0.79 w.r.t water
>Gas Sp. Gra 0.65 w.r.t air
>Gas Flow Rate 2000 scfh
>Liquid flow rate 5 gallons/day (Approximately)
>Micron of Gas required 0.03 to 0.08
>
NOTE-1: The Micron of Gas I assume considering the fact that Tobacco Smoke particales are in the range of 0.01 to 0.1
Note-2: No electricity available at site
In my opinion insllation of a filter separator will knock the liquid and solid particles down to 5 microns. Addition of a coalescer will bring the particle size to <1 micron. Beyond this it is realy a difficult task.
Do you think the addition of a vessel containing a mixuture of activated Charcoal and physically drying agent(Type: Alumina)will improve the fuel gas quality?
Since, the possibility of carry over of Charcoal particles and drying agent is there therefore, a <0.1 micron or smaller filter would work to safeguard the instruments from being damaged?
I would like your comments and recommendations to come up with practical and economical solution.
It is desired to improve the fuel gas by knocking down the heavy hydrocarbons and moisture (if present) at remote location.
The typical composition of gas at wellhead is here under:
Component Mole %
>H2S 0.0
>CO2 1.43
>N2 14.9
>C1 51.24
>C2 7.72
>C3 8.25
>C4 4.01
>C4 5.69
>C5 3.12
>C5 2.07
>C6 1.27
>C7 + 0.3
>Total 100%
Operatining pressure minimum 85 Max. 100 psig
>Design pressure 150# rating
>Design Temp 150 deg. F
>Operating TEmp 115 deg. F
>Liquid Spec. Gr 0.79 w.r.t water
>Gas Sp. Gra 0.65 w.r.t air
>Gas Flow Rate 2000 scfh
>Liquid flow rate 5 gallons/day (Approximately)
>Micron of Gas required 0.03 to 0.08
>
NOTE-1: The Micron of Gas I assume considering the fact that Tobacco Smoke particales are in the range of 0.01 to 0.1
Note-2: No electricity available at site
In my opinion insllation of a filter separator will knock the liquid and solid particles down to 5 microns. Addition of a coalescer will bring the particle size to <1 micron. Beyond this it is realy a difficult task.
Do you think the addition of a vessel containing a mixuture of activated Charcoal and physically drying agent(Type: Alumina)will improve the fuel gas quality?
Since, the possibility of carry over of Charcoal particles and drying agent is there therefore, a <0.1 micron or smaller filter would work to safeguard the instruments from being damaged?
I would like your comments and recommendations to come up with practical and economical solution.