Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations IDS on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

duct material for underground odor control

Status
Not open for further replies.

fcxdfm

Mechanical
Apr 19, 2006
44
What's the best duct material for the underground odor (H2S) control exhaust duct? FRP, HDPE or PVC schedule 80? The vacuum pressure of the exhaust system is about 5 inch...

Thanks!!!
 
Replies continue below

Recommended for you

CPVC (chlorinated PVC) duct would be better than PVC, PVC would likely be the best option of the selected plastics you have noted. CPVC has better compatibility with H2S if it is wet.

See the attached website for chemical compatibility.

 
the duct materials must comply with ul-181 ..... no?

insulated? ...... no?

i'd use frp ..... spunstrand, harrington, ershings, primary plastics, etc
 
Status