- Dec 13, 2017
- 38
Hello
I am upgrading an old 1980's Office that uses circular duct throughout for HVAC. I want to retain the old circular duct downstream of the air handler as much as possible up as far as new VAV boxes I intend installing..
I usually use 1pa/m when sizing ductwork and that is how I intend sizing the duct down stream of the new VAV boxes.
However can I go up to 1.5pa/m for the main circular duct serving these VAV boxes with a max velocity of approximately 7.5m/s?...duct are mostly 300-400mm dia. off the air handlers main supply header.
Regards
W