scottlsu
Mechanical
- Mar 13, 2011
- 10
I am currently working on a problem with a 20,000cfm VAV AHU. This has system powered terminal units (Carrier Moduline) which require 1" of static at the terminal unit in order to modulate. The problem is that there is not enough static pressure at most of the units for them to modulate. This is a roughly 30 year old setup, which I don't believe has ever had the ability to modulate.
I believe the fan was undersized to begin with. It was originally specified with a 20,000 @ 1.5" esp fan, which is currently in place. I am trying to specify a new fan which will provide 1" of static pressure at the furthest terminal. Can anyone assist me with a general approach to modeling this? If i am lacking .5" at the furthest terminal, I do not think it is as easy as adding .5" to the new fan specs, as i highly doubt this thing responds linearly.
I have tried using Revit MEP, however this does not allow you to simulate different static pressure conditions (it basically adds up all of the pressure drops to calculate ESP).
Please help!
I believe the fan was undersized to begin with. It was originally specified with a 20,000 @ 1.5" esp fan, which is currently in place. I am trying to specify a new fan which will provide 1" of static pressure at the furthest terminal. Can anyone assist me with a general approach to modeling this? If i am lacking .5" at the furthest terminal, I do not think it is as easy as adding .5" to the new fan specs, as i highly doubt this thing responds linearly.
I have tried using Revit MEP, however this does not allow you to simulate different static pressure conditions (it basically adds up all of the pressure drops to calculate ESP).
Please help!