demar
Mechanical
- Feb 26, 2002
- 4
I have a VAV air-handler with a DX cooling coil (two-circuits, intertwined) with a two-stage condensing unit (operates on its own pressure controls). The unit also has hot gas bypass (mechanical type) to allow compressor operation at low loads. Due to 'cold blow' complaints when the boxes are at minimum flow and the thermostat is satisfied, we added discharge air reset to the control strategy (based on OA air temp.: 60deg OA, DAT=50; @40deg OA, DAT=60). However, the compressor cycles off more often (with 5 min. time delay) resulting in poor DAT control and more complaints. I think this happens because the DAT is at a higher value, say 60, and the hot gas bypass valve doesn't have a chance to operate before the DAT differential shuts the compressor down. If you have any experience with this, I would sure appreciate some help!!!