At two different stations, I took phase angles from A phase PT on 115kv bus to A B & C metering PTs on 13.8kv bus. I used a Dranetz Phasemeter - model 314. Both transformers are Dy1 and grid is A-B-C CCW.
The station with A-B-C sequence read:
HV A leads LV A by 32 deg
HV A leads LV B by 152 deg
HV A leads LV C by 272 deg
The station with A-C-B sequence read:
HV A leads LV A by 333 deg
HV A leads LV B by 93 deg
HV A leads LV C by 215 deg
When you draw two circles and plot the phases they both indicate A-B-C with CCW phasor rotation.
At the A-C-B station, I expected B and C angles to be the opposite in order to show A-C-B sequence.
Do these readings look correct? Please explain. Thanks