dfdt
Electrical
- Sep 10, 2002
- 118
I would like to hear your comments/views on following
We have single 6.6kV distribution feeder being supplied by ungrounded source via 110 kV(ungrounded star wdg)/6.6kV(delta wdg)transformer. Although technically speaking if we have earth fault on this feeder the earth fault current would be 3 times of steady state phase to ground capacitive current as voltages of healthy phases will rise to √3 times. My question is that "can we use this rise in voltage (from VLL/√3 to VLL) for detecting earth faults on ungrounded system?
We have single 6.6kV distribution feeder being supplied by ungrounded source via 110 kV(ungrounded star wdg)/6.6kV(delta wdg)transformer. Although technically speaking if we have earth fault on this feeder the earth fault current would be 3 times of steady state phase to ground capacitive current as voltages of healthy phases will rise to √3 times. My question is that "can we use this rise in voltage (from VLL/√3 to VLL) for detecting earth faults on ungrounded system?