vennivivi
Electrical
- Jan 15, 2007
- 45
Hi,
My transformer, ONAN 3,0 MVA 11 k V/ 400 v , used to trip on earth fault protection. I have got a zero sequence CT wired to my relay with a setting of 0,1 A instantaneous.We had four trips in the last week. The transformer has been sucessfully megerred, PI > 5 , and di-electric test also ok. After a trip, the transformer is powered and run fine for hours.
I have also got an overcurrent earth fault relay which used summation current for earth fault protection. The relay saw IDMT on one phase.
Any guess on the setting.
Grundig
My transformer, ONAN 3,0 MVA 11 k V/ 400 v , used to trip on earth fault protection. I have got a zero sequence CT wired to my relay with a setting of 0,1 A instantaneous.We had four trips in the last week. The transformer has been sucessfully megerred, PI > 5 , and di-electric test also ok. After a trip, the transformer is powered and run fine for hours.
I have also got an overcurrent earth fault relay which used summation current for earth fault protection. The relay saw IDMT on one phase.
Any guess on the setting.
Grundig