markjp
Electrical
- May 28, 2007
- 13
I was wondering if someone may have an opinion on the following issue. I have started working on a project for an underground mine and have noticed that the earth leakage relays on the 1000V motor circuits are wired to trip the contactor rather than the circuit breaker. I've have always seen earth leakage relays as a fault protection device and as such should be used to trip the circuit breaker via shunt trip, as a contactor isn't designed to interrupt large fault currents. Details of the installation are as follows: 1000V,3-phase fault level up to 25kA, NER limiting earth fault to 5A, earth leakage relays set to 500mA & 100ms, typical motor circuit with circuit breaker, electronic overload relay and contactor, 110kW and 7.5kW pumps. Theoretically the contactor should not have to operate under a fault condition where there is more than 5A earth fault current due to the NER. Also the 100ms time delay on the earth leakage relay should see the circuit breaker operate faster (say 50ms)to clear the fault under a major fault condition. So I suppose the installation looks okay but am looking for other opinions on the issue as I just haven't seen it done this way before. Thanks.