Earthing Mesh Design 1

Status
Not open for further replies.

Selva_51

Electrical
May 10, 2024
7
Hi All,
We are in the midst of designing a hybrid power plant with solar PV, BESS and DG with a 15kV substation (with step up transformer and MV switchgear). For this to prepare a earthing mesh design as per IEEE 80 could you please let me know if I create an individual mesh for the substation, control building and the solar farm and connect all the meshes together in parallel. When I do an individual calculation for Rg,step and touch potential for each of these sections. I observe an attainable Step and touch voltage of more than the system voltage of 480/277V for the control building. Why is this so? and should we calculate the step and touch voltages for the LV side as well? TIA
 
Replies continue below

Recommended for you

The GPR -Ground Potential Rise -it is connected to premises far from the Power Station and only the fault current from an outside station or to an outside station or line which return path is through ground , may rise this potential. So, if a system-480 V, for instance-including power transformer or other power source-and the receiving installations are located entirely on a power station grid the return current of the ground fault occurs through grid and not through ground and doesn't produce GPR.
For Generation Power Station Grounding IEEE 665/1995 standard may help [even it is Withdrawn now!].
 