Earthing of Gensets During Factory Testing

Status
Not open for further replies.

genhead

Electrical
Jul 26, 2001
71
We are a supplier of new and used low voltage (415v)generators.
During factory testing before despatch, how should the gensets be earthed ? My main concern is operator safety.
Most of the gensets don't have earth leakage protection.
The neutral is connected to the main earth terminal in the generator terminal box.
 
Replies continue below

Recommended for you

Suggestion: It would be prudent to start the generator tests with high-resistance system grounding since one fault at the generator load would be tolerated, monitored, fault location determined. If only the solidly grounded neutral system grounding is applied, a ground fault current or arcing can cause more extensive damages than the generator the high-resistance system grounding, for example.
 

In addition to earthing/grounding, do not overlook bonding of exposed conductive surfaces to limit potential difference and consequent shock hazard, and facilitate operation of overcurrent devices.
 