rex2704
Electrical
- Nov 22, 2006
- 14
I am working on a substation design using SKM power tools software (version 6.0). While working with the software, I have noticed that delta connected capacitor banks used for power factor correction give rise to ground fault currents in an ungrounded delta connected system.
I had used a delta/delta transformer to feed an MCC with motor and non-motor loads along with PFC capacitors. I had used delta connection for all my loads as well as for the capacitors. A 300kVAR capacitor bank on a 480V bus gave me a SLG fault current of 2500A. When I disconnect the capacitors from the system, I get zero ground fault current which is correct.
I do not know how to represent capacitance in the positive, negative and zero sequence impedance diagrams for SLG fault current calculation. So I am not able to understand this phenomena at all.
I would appreciate every help to explain this behavior to me.
Thank you every one in advance!
I had used a delta/delta transformer to feed an MCC with motor and non-motor loads along with PFC capacitors. I had used delta connection for all my loads as well as for the capacitors. A 300kVAR capacitor bank on a 480V bus gave me a SLG fault current of 2500A. When I disconnect the capacitors from the system, I get zero ground fault current which is correct.