yk052052
Electrical
- Mar 16, 2016
- 14
In our plant, electric system consists of 35kV/6kV/400V. (Current voltages are approximately 35kV/6.2kV/413V)
We ran the MV motor (6kV, 3100kw) connected to soft starter. It took around 14Sec until bypass mode and once current reached at the starting current(around 1540A), it stayed at the starting current until bypass mode(10-11 Sec.
We measured the voltage dip at each system and found as below.
35kV -> 33kV
6.2kV -> 5.2kV (Upstream TR capacity is 10MVA)
413V -> 345V (Upstream TR capacity is 2.5MVA)
We're concerned about voltage dip that is larger than our expect.
Our 27 is set to 80% of each rated voltage so protection didn't operate. But I'm not sure this voltage dip at this duration is ok for loads at downstream(especially motor loads).
Do you think this situation is fine? If not, what can we try to solve this issue?
We ran the MV motor (6kV, 3100kw) connected to soft starter. It took around 14Sec until bypass mode and once current reached at the starting current(around 1540A), it stayed at the starting current until bypass mode(10-11 Sec.
We measured the voltage dip at each system and found as below.
35kV -> 33kV
6.2kV -> 5.2kV (Upstream TR capacity is 10MVA)
413V -> 345V (Upstream TR capacity is 2.5MVA)
We're concerned about voltage dip that is larger than our expect.
Our 27 is set to 80% of each rated voltage so protection didn't operate. But I'm not sure this voltage dip at this duration is ok for loads at downstream(especially motor loads).
Do you think this situation is fine? If not, what can we try to solve this issue?