Help needed in sizing equipment grounding conductor when cable are installed in parallel, in cable tray.
Setup:
Ambient Temp Max. 30C
Seconday Unit-Substation
Pri OCPD: 4,160V Fused Switch, 300E Fuse
XF Pri Feeder: 3/C-250kcmil w/ #3 Gnd, MV-90
XF: 1500kVA, 480Y/277V, 5.75%, Dry
XF Sec Feeder: 6-3/C-500kcmil w/ #2 Gnd, Type TC
Sec OCPD: 480V LV MCC Main CB, 2000A
Raceway: Uncovered Cable Tray
Notes:
1) The transformer secondary conductors are installed in parallel.
2) No ground fault protection is included on the transformer primary, or at the MCC main.
3) Would prefer to use standard cable manufacturer's offerings for multiconductor power cable configurations.
Question:
Does the code (NEC) allow installation of "supplementary" equipment grounding conductors to meet
the intent of 250.122?
i.e. Could additional ground cabling be installed in addition to those already included with the phase conductor
cables to increase the overall, or "total" size of the EGC?
If so, how would the supplementary conductors be sized?
My initial thought it that the EGC should be equivalent in size to a 250kcmil per Table 250.122.
So, with the #2 already included in the multi-conductor cable, we could install another single #4/0 next to each cable.
#2 = 0.067in2
#4/0 = 0.219in2
250kmcil = 0.260in2
0.219 + 0.067 = 0.286
Thanks in advance for your suggestions and comments.
EETD
Setup:
Ambient Temp Max. 30C
Seconday Unit-Substation
Pri OCPD: 4,160V Fused Switch, 300E Fuse
XF Pri Feeder: 3/C-250kcmil w/ #3 Gnd, MV-90
XF: 1500kVA, 480Y/277V, 5.75%, Dry
XF Sec Feeder: 6-3/C-500kcmil w/ #2 Gnd, Type TC
Sec OCPD: 480V LV MCC Main CB, 2000A
Raceway: Uncovered Cable Tray
Notes:
1) The transformer secondary conductors are installed in parallel.
2) No ground fault protection is included on the transformer primary, or at the MCC main.
3) Would prefer to use standard cable manufacturer's offerings for multiconductor power cable configurations.
Question:
Does the code (NEC) allow installation of "supplementary" equipment grounding conductors to meet
the intent of 250.122?
i.e. Could additional ground cabling be installed in addition to those already included with the phase conductor
cables to increase the overall, or "total" size of the EGC?
If so, how would the supplementary conductors be sized?
My initial thought it that the EGC should be equivalent in size to a 250kcmil per Table 250.122.
So, with the #2 already included in the multi-conductor cable, we could install another single #4/0 next to each cable.
#2 = 0.067in2
#4/0 = 0.219in2
250kmcil = 0.260in2
0.219 + 0.067 = 0.286
Thanks in advance for your suggestions and comments.
EETD