ELECTRIC ARC FURNACE 1

Status
Not open for further replies.

Elec777

Electrical
Apr 24, 2010
38
WE WILL BE HAVING IN OUR COMPANY AN ELECTRIC ARC FURNACE NEXT YEAR,

IS IT POSSIBLE TO FEED THE SAID FURNACE BY DIESEL GENERATORS?
 
Replies continue below

Recommended for you

Hi Bill,

Straying a little outside my normal world, but the TSO's priority will be to minimise the disturbance on their system, which means having sufficient transformer impedance to decouple the EAF from the transmission substation. With (I'm guessing a little here) 15% - 20% impedance you're looking at a substantial fault current on the LV side and if there's a fairly direct connection to the transmission system then the EAF transformer impedance is going to be the dominant factor in determining the fault current.

Hopefully someone like prc will have a bit more knowledge of EAF transformers themselves, but my understanding isn't so much that the fault level is abnormally high as the transformer and ancillaries like the tapchanger are designed to handle sustained and repetitive fault-level currents on a more-or-less continuous basis.
 
Thanks Scotty.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 