Can Somebody tell me why this Works?
The Motor’s are a standard 230/460V-60hz 12 lead motor. They have this special connection that allows the motor to not be de-rated and run @ 380V-50hz with a 1.15 service factor. How’s does the Ground help this system? Any Ideas’s would be greatly appreciated.
Circuit Connection on 12 Lead motor
Leg 1 2-8
Leg 2 3-9
Leg 3 1-7
4-5-6-10-11-12 tied together and sent to Ground
With a Note
1.732 x low votlage
Operating at over 600V Neutral on 1.732 x l.v. must be solidly grounded
The Motor’s are a standard 230/460V-60hz 12 lead motor. They have this special connection that allows the motor to not be de-rated and run @ 380V-50hz with a 1.15 service factor. How’s does the Ground help this system? Any Ideas’s would be greatly appreciated.
Circuit Connection on 12 Lead motor
Leg 1 2-8
Leg 2 3-9
Leg 3 1-7
4-5-6-10-11-12 tied together and sent to Ground
With a Note
1.732 x low votlage
Operating at over 600V Neutral on 1.732 x l.v. must be solidly grounded